[TRNSYS-users] Virtual window error
Knut Erik Enerstvedt
knut.erik.enerstvedt at gmail.com
Tue Nov 16 03:51:59 PST 2010
Dear Sumaila Aongya,
Try the virtual window with WinID 10001 (Basic or American library) instead.
I also get this error with WinID 1.
Best regards,
Knut Erik Enerstvedt
>Hello,
>I am simulating a building using TRNSYS 17. On the recommendation of M.
Kummert, instead of using a wall made of air to represent >hallways or lack
of a wall from a zone to another one, we changed them into virtual/non
existant windows (WinID: 0001) with tiny frames >(2% of surface area). Now,
the problem is that the simulation cannot run the model because it's
creating an error UNIT7, TYPE 56 " >iniglasdata: value negative or greater
than 1 for nonvisual absorption W4_front was found after fitting for
Window-ID. 1: abs_nonvis= >-0.008717874 at angle= 0." I get this error
with horizontal and vertical windows but if I simulate the same
building with real windows i.e. >7433 instead of virtual ones, it works
perfectly.
>We changed to virtual windows because it's supposed to represent more
effectively thermal resistance and others properties. Can I >change some
configurations so this error doesn't come back? Should I just keep the air
walls, since the difference in properties are >almost negligeable?
>Can you help me with this?
>Thanks!
*>Sumaila Aongya*
>Stagiaire universitaire
>Laboratoire des technologies de l'énergie (LTE)
>600, avenue de la Montagne
>Shawinigan, QC, G9N 7N5
>Tel: 819-539-1400 poste 1340
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101116/4f503a22/attachment-0005.htm>
More information about the TRNSYS-users
mailing list