[TRNSYS-users] How to calculate the zone thermal time constant &	air volume flow of opening
    王洋 
    wanghongyang1767 at gmail.com
       
    Wed Nov  3 07:29:36 PDT 2010
    
    
  
Dear all,
1. How to calculate or find the thermal time constant of zone in TRNSYS
software?
---------- WALL TYPE BST_FL_HEAT_W1      ----------
       THERMAL CONDUCTANCE, U=    67.80000 kJ/h m2K; U-Wert=     4.48235
W/m2K
              (incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
                        TRANSFERFUNCTION COEFFICIENTS
   K            A              B              C              D
   0       1.7050117E+02    2.1087019E+01    1.7050117E+02    1.0000000E+00
   1      -1.1800059E+02    3.5808933E+01   -1.1800059E+02   -1.3683139E-01
   2       6.0267372E+00    1.6298573E+00    6.0267372E+00    4.7362566E-05
   3      -1.2736107E-03    2.3363784E-04   -1.2736107E-03
  SUM      5.8526043E+01    5.8526043E+01    5.8526043E+01    8.6321597E-01
What's meaning of A B C D? Are they Wall's TRANSFERFUNCTION COEFFICIENTS?
And what is the thermal time constant of the whole zone? How to calculate or
find the thermal time constant of the whole zone in TRNSYS software?
Need I   calculate by myself the whole zone's TRANSFERFUNCTION based on all
the walls of the zone or others?
2.  How to calculate or find air volume flow of the window opening in
TRNFlow software?
The window opening area (m2)is known. Whether it needs the wind speed(m/s)
or not?
Many thanks!
Br.
wang
2010/11/3 <trnsys-users-request at cae.wisc.edu>
> Send TRNSYS-users mailing list submissions to
>        trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
>        https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
>        trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
>        trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
>   1. Re: GenOpt optimization: problem for the second generation
>      after 5 simulations (Thibaut VITTE)
>   2. Re: google sketchup+trnsys3d (hotline)
>   3. input file (Emiliano Casati - 3ME)
>   4. Re: GenOpt optimization: problem for the secondgeneration
>      after 5 simulations (Timothy McDowell)
>
>
> ---------- 已转发邮件 ----------
> From: Thibaut VITTE <thibaut.vitte at h3c-energies.fr>
> To: trnsys-users at cae.wisc.edu
> Date: Wed, 03 Nov 2010 11:27:53 +0100
> Subject: Re: [TRNSYS-users] GenOpt optimization: problem for the second
> generation after 5 simulations
> Dear Alexis,
>
> I've had a similar error when I used Genopt. I've had several components
> tracked by a "trace" command that made my list file enormous (more than
> 100Mb) and genopt could'nt handle that amount of data.
>
> Just my 2cents.
>
> Thibaut
> --
>
> Le futur maîtrisé
>
>  Thibaut VITTE
>
> Docteur - Ingénieur Energies
>
> Mail : thibaut.vitte at h3c-energies.fr
>
> -----------------------------
>
> H3C-énergies
>
> 35, chemin du vieux Chêne - 38240 MEYLAN
>
> Tél : 04 76 41 88 66  Fax : 04 76 41 28 94
>
> www.h3c-energies.fr
>
>
> -----------------------------------------------------------------------------------
>
> Afin de contribuer au respect de l'environnement, merci de n'imprimer ce
> message qu'en cas de nécessité.
>
> In order to respect the environment, please don't print this e-mail unless
> you really need to.
>
>
>
> ---------- 已转发邮件 ----------
> From: "hotline" <hotline at transsolar.com>
> To: "julia.feste" <julia.feste at whitepavilion.com.cn>
> Date: Wed, 3 Nov 2010 11:37:08 +0100
> Subject: Re: [TRNSYS-users] google sketchup+trnsys3d
> Hi,
>
> that's a well known problem that will be fixed in the next version.
> Hopefully upcoming within the next weeks.
>
> Regards
> Christian
>
> TRANSSOLAR Software Team
> hotline at transsolar.com
>
> www.trnsys.de
> Transsolar KlimaEngineering - Technologien für energieeffizientes Bauen
> und Nutzerkomfort in Gebäuden
> Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart /
> Amtsgericht Stuttgart - HRB 23347 / USt-IdNr.: 99073/00911
> Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
> Dipl.Phys. Stefan Holst, Prof. Volkmar Bleicher
>
> -----Ursprüngliche Nachricht-----
> Von: julia.feste [mailto:julia.feste at whitepavilion.com.cn]
> Gesendet: Mittwoch, 3. November 2010 06:46
> An: trnsys-users at cae.wisc.edu
> Betreff: [TRNSYS-users] google sketchup+trnsys3d
>
>
> Hello everybody,
> Thanks for your posts that's always really interesting!
> I come up with a problem using Google Sketchup and TRNSYS3D: inside a
> TRNSYS zone, I draft a square, then I want to pull it up at a certain
> height, so I write the number then Enter, and this error appears:
>
> <-----Beginning of the error----->
> ERROR:
> NoMethodError
> undefined method `position' for
> #<Sketchup::AttributeDictionary:0xfcb4eb8>
>
> BACKTRACE:
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `polygon_loop'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `each'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `polygon_loop'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:321:in `outer_polygon'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:326:in `polygon'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:27:in
> `detect_base_face'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:20:in `each'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:20:in
> `detect_base_face'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:254:in `face_polygon'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:253:in `each'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:253:in `face_polygon'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/interfaces/Surface.rb:107:in
> `update_input_object'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:94:in
> `update_input_object'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/interfaces/DrawingInterface.rb:353:in
> `on_change_entity'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/observers/FaceObserver.rb:32:in `onChangeEntity'
> C:/Program Files/Google/Google SketchUp
> 8/Plugins/Trnsys3d/lib/AsynchProc.rb:17:in `initialize'
>
> <-----End of the error----->
>
> When I pull it up manual, I don't have any problem, just when I write
> the number.
>
> Thanks in advance for your help,
> Julia.
> ________________________________________
> From: trnsys-users-request at cae.wisc.edu
> [trnsys-users-request at cae.wisc.edu]
> Sent: Wednesday, November 03, 2010 1:04 AM
> To: trnsys-users at cae.wisc.edu
> Subject: TRNSYS-users Digest, Vol 71, Issue 4
>
> Send TRNSYS-users mailing list submissions to
>        trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
>        https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
>        trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
>        trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific than
> "Re: Contents of TRNSYS-users digest..."
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
>
>
>
>
>
> ---------- 已转发邮件 ----------
> From: "Emiliano Casati - 3ME" <E.I.M.Casati at tudelft.nl>
> To: <trnsys-users at cae.wisc.edu>
> Date: Wed, 3 Nov 2010 13:19:58 +0100
> Subject: [TRNSYS-users] input file
>
> Hi to everybody!
>
> I don’t understand why, for certain projects, I can’t open the input file,
> the message is “the system cannot find the path specified”.
>
> Where should I find the input file?
>
>
>
> Thanks a lot
>
>
>
> ec
>
>
> ---------- 已转发邮件 ----------
> From: "Timothy McDowell" <mcdowell at tess-inc.com>
> To: "Thibaut VITTE" <thibaut.vitte at h3c-energies.fr>,
> trnsys-users at cae.wisc.edu
> Date: Wed, 3 Nov 2010 07:23:05 -0500 (CDT)
> Subject: Re: [TRNSYS-users] GenOpt optimization: problem for the
> secondgeneration after 5 simulations
> This type of error in GenOpt is usually caused by an error in the TRNSYS
> simulation.  You need to check the *.lst file for the TRNSYS run to see
> what the TRNSYS error is.
>
> Regards,
>
> Tim
>
>
>
>
>
> ----------------------------------
> Timothy McDowell
> Executive Vice President
> Thermal Energy System Specialists, LLC
> 22 N. Carroll St, Suite 370
> Madison, WI 53703
> Phone: 608-274-2577
> Fax: 608-278-1475
>
> ----- Original Message -----
> From: "Thibaut VITTE" <thibaut.vitte at h3c-energies.fr>
> Sent: Wed, November 3, 2010 5:27
> Subject:Re: [TRNSYS-users] GenOpt optimization: problem for the
> secondgeneration after 5 simulations
>
>
>
>
>
>
>
>
>
>    Dear Alexis,
>
>    I've had a similar error when I used Genopt. I've had several
>    components tracked by a "trace" command that made my list file
>    enormous (more than 100Mb) and genopt could'nt handle that amount of
>    data.
>
>    Just my 2cents.
>
>    Thibaut
>    --
>
>
> .bodyclass      @page { size: 8.5in 11in; margin-top: 0.7874in;
> margin-bottom:
> 0.7874in; margin-left: 0.7874in; margin-right: 0.7874in }
> .bodyclass      table { border-collapse:collapse; border-spacing:0;
> empty-cells:show }
> .bodyclass      td, th { vertical-align:top; font-size:12pt;}
> .bodyclass      h1, h2, h3, h4, h5, h6 { clear:both }
> .bodyclass      ol, ul { margin:0; padding:0;}
> .bodyclass      li { list-style: none; margin:0; padding:0;}
> .bodyclass      li span.odfLiEnd { clear: both; line-height:0; width:0;
> height:0; margin:0; padding:0; }
> .bodyclass      span.footnodeNumber { padding-right:1em; }
> .bodyclass      * { margin:0; }
> .bodyclass      .fr1 { font-size:12pt; text-align:center;
> vertical-align:top;
> margin-left:0in; margin-right:0in; margin-top:0in; margin-bottom:0in;
> padding:0in; border-style:none; }
> .bodyclass      .P1 { font-size:12pt; margin-bottom:0in; margin-top:0in;
> font-family:Times New Roman; text-align:center ! important; }
> .bodyclass      .P10 { font-size:7.5pt; margin-bottom:0in; margin-top:0in;
> font-family:Tahoma, sans-serif; text-align:justify ! important;
> color:#f79646; }
> .bodyclass      .P2 { font-size:9pt; margin-bottom:0in; margin-top:0in;
> font-family:Tahoma, sans-serif; text-align:center ! important;
> color:#e36c0a; font-style:italic; font-weight:bold; }
> .bodyclass      .P3 { font-size:9pt; margin-bottom:0in; margin-top:0in;
> font-family:Tahoma, sans-serif; text-align:justify ! important;
> color:#e36c0a; font-weight:bold; }
> .bodyclass      .P4 { font-size:9pt; margin-bottom:0in; margin-top:0in;
> font-family:Tahoma, sans-serif; text-align:justify ! important;
> color:#e36c0a; font-weight:bold; }
> .bodyclass      .P5 { font-size:7.5pt; margin-bottom:0in; margin-top:0in;
> font-family:Tahoma, sans-serif; color:#e36c0a; font-weight:bold; }
> .bodyclass      .P6 { font-size:7.5pt; margin-bottom:0in; margin-top:0in;
> font-family:Tahoma, sans-serif; text-align:justify ! important;
> color:#3329b1; }
> .bodyclass      .P61 { font-size:8.5pt; margin-bottom:0in; margin-top:0in;
> font-family:Tahoma, sans-serif; text-align:justify ! important;
> color:#3329b1; }
> .bodyclass      .P7 { font-size:7.5pt; margin-bottom:0in; margin-top:0in;
> font-family:Tahoma, sans-serif; text-align:justify ! important;
> color:#3329b1; font-style:italic; }
> .bodyclass      .P8 { font-size:7.5pt; margin-bottom:0in; margin-top:0in;
> font-family:Tahoma, sans-serif; text-align:justify ! important;
> color:#3329b1; font-style:italic; }
> .bodyclass      .P9 { font-size:12pt; margin-bottom:0in; margin-top:0in;
> font-family:Times New Roman; text-align:justify ! important; }
> .bodyclass      .P91 { font-size:12pt; margin-bottom:0in;
> margin-top:0.05in;
> font-family:Times New Roman; text-align:justify ! important; }
> .bodyclass      .Standard { font-size:12pt; font-family:Times New Roman; }
> .bodyclass      .T1 { color:#f79646; }
> .bodyclass      .T2 { color:#f79646; font-family:Tahoma, sans-serif;
> font-size:7.5pt; }
> .bodyclass      .T3 { color:#3329b1; font-family:Tahoma, sans-serif;
> font-size:7.5pt; }
> .bodyclass      { }
>
>
>
>
>
>
>
>
>
>
>                  Le futur maîtrisé
>
>
>
>
>
>
>
>              Thibaut VITTE
>              Docteur - Ingénieur Energies
>              Mail : thibaut.vitte at h3c-energies.fr
>
>              -----------------------------
>              H3C-énergies
>              35, chemin du vieux Chêne - 38240 MEYLAN
>              Tél : 04 76 41 88 66 – Fax : 04 76 41 28
>                  94
>              www.h3c-energies.fr
>
>
>
>
>
>
>
>
>  -----------------------------------------------------------------------------------
>      Afin de contribuer au respect de l'environnement,
>        merci de n'imprimer ce message qu'en cas de nécessité.
>      In order to respect the environment, please don't
>        print this e-mail unless you really need to.
>
>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
> ----- End of original message -----
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101103/93def484/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo.gif
Type: image/gif
Size: 2701 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101103/93def484/attachment-0005.gif>
    
    
More information about the TRNSYS-users
mailing list