[TRNSYS-users] Chilled Ceiling QCOMI
Kersken, Matthias
Matthias.Kersken at ibp.fraunhofer.de
Sun Nov 21 23:54:24 PST 2010
Dear Mr. Vazquez!
QCOMI contains only convection and IR-exchange to other surfaces of the
zone.
Solar gains (diffuse radiation for a ceiling), IR-energy from internal Heat
sources (Heating, artificial lightning, ...) and wallgains are NOT included.
This energy flows are calculation in QABSI.
(Manual 5-26)
In order to have a complete energy balance for Your ceiling You should
compare the sum (attention! +/-) of this values with Your cooling demand.
With kind regards,
Matthias Kersken
---
Dipl.-Ing. Matthias Kersken
Wissenschaftlicher Mitarbeiter / Abteilung Energiesysteme
Fraunhofer-Institut für Bauphysik
Institutsteil Holzkirchen
Fraunhoferstraße 10
83626 Valley
eMail: Matthias.Kersken at ibp.fraunhofer.de
Telefon 08024 / 643-204
Telefax 08024 / 643-366
www.ibp.fraunhofer.de <http://www.ibp.fraunhofer.de/>
Dipl.-Ing. Matthias Kersken
Research Associate / Department Energy Systems
Fraunhofer Institute for Building Physics
Branch Holzkirchen
Fraunhoferstraße 10
D-83626 Valley
eMail: <mailto:Matthias.Kersken at ibp.fraunhofer.de>
Matthias.Kersken at ibp.fraunhofer.de
Phone +49 8024 / 643-204
Fax +49 8024 / 643-366
<http://www.ibp.fraunhofer.de/> www.ibp.fraunhofer.de
---
_____
Von: Mavi Cambronero Vázquez [mailto:maviqnk at gmail.com]
Gesendet: Freitag, 19. November 2010 10:52
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Chilled Ceiling QCOMI
Hi,
Something wrong is happening when I run my simulation with a chilled
ceiling. Until now I though the output QCOMI was the energy from the room to
the wall and it should be similar to the demand of cooling of my room. Why
are so different QCOMI and the theorical calculation:
Energy = flow_ceiling*cp_water*(Texit_water-Tentry_water)?
THanks
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101122/09345545/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smime.p7s
Type: application/x-pkcs7-signature
Size: 7103 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101122/09345545/attachment-0001.bin>
More information about the TRNSYS-users
mailing list