[TRNSYS-users] Zone capacitance

David BRADLEY d.bradley at tess-inc.com
Thu Nov 18 09:23:31 PST 2010


The default capacitance (1.2*ZoneVolume) takes into account the 
capacitance of the zone air only. Typically a value 5 times the default 
is appropriate to include the capacitance of the room furnishings.
Regards,
  David


On 11/18/2010 05:14, Tran Thanh Vu wrote:
> Hi everyone
>
>    I'm trying to simulate zone and cooling coil with external load
> profile by using type 690, but I have difficult when deciding zone
> capacitance. May someone give me some instruction to calculate this value.
>
> Thank in advance
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com




More information about the TRNSYS-users mailing list