[TRNSYS-users] TYPE 109
knut.erik.enerstvedt at niva.no
knut.erik.enerstvedt at niva.no
Thu May 20 00:11:29 PDT 2010
Dear Samar,
I suggest you check the values of <interp> and <samp> in your data file
(see documentation 5-478) to make sure that your radiation data is not
interpolated and that the correct time interval is specified. Also, be
aware that while radiation input to type 109 is in units of W/m2, output
is in units of kJ/hr,m2.
Best regards,
Knut Erik Enerstvedt
>Dear Sir/Madam,
>Any one has an experience with TYPE 109-User defined?
>I am facing a problem with solar radiation. I have the diffuse solar on
>horizontal surface (IdH), Normal Solar Radiation (IDN).
>I inserted it with notepad as corresponding to IBEAM_N, IDIFF_H
respectively.
>but when I am trying to redraw these data it gives me totally different
of the
>source data.
>Thank you and Best Rgards,
>Samar
------------------------------------------------------------------------------------------------------------