[TRNSYS-users] Simplified heating and cooling based on operativetemperature

David Bradley bradley at tess-inc.com
Wed Mar 31 08:29:02 PDT 2010


Sabine,

>   1.    _it takes two timesteps for the ideal heating to reach the 
> required setpoint_..
>
>         Is this normal or what am I doing wrong?
>
if you have limited the capacity of the heating type in TRNBuild, it 
could take some time for the building to reach its setpoint. If you have 
unlimited heating capacity then it should reach the new heating 
temperature instantly. However, Type65 (the online plot) only plots one 
point per time step and it draws a line between points; looking at the 
figures that you attached, I think you are just seeing Type65's 
interpolation. If you hold down both the SHIFT and CTRL keys at the same 
time and move your mouse around the plot, you'll see the ACTUAL value of 
each output (not the interpolated value that Type65 is showing you. You 
can prove it to yourself as well by changing to a shorter timestep - 
you'll see that it appears now as though it takes less time to reach 
setpoint.
>
>         2.   When using a schedule in trnbuild (so not in the
>         operative correction trick of above), somehow _the heating
>         only switches on at exactly the time of the switch_ (in my
>         case 7 h and 17 h), while I assumed the schedule to mean that
>         at the new time the new temperature must be obtained (see
>         attached document). The heating switches OFF at exactly the
>         changing time, so it then takes the new setpoint temperature.
>         (see figure 2).
>
again, I think this is purely a matter of how the online is plotting the 
results (one point per timestep).
>
>         3.   Does anyone know why the temperature seems to be
>         fluctuating a little (in other words: it is not a smooth line)
>         as soon as the heating turns off?
>
>         Also when using a smaller timestep the line is not smooth, but
>         the temperatures stay constant during a hour, so the line
>         looks like a staircase..
>
>              (note: the non-smooth line occurs when the heating is OFF)
>
I think Arie's response is the most probable one here.
Best,
 David



-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100331/3f16f049/attachment-0005.htm>


More information about the TRNSYS-users mailing list