Fred,
 I think you might be confusing efficiency and effectiveness. 
Effectiveness is actual energy transfer divided by maximum theoretically 
possible energy transfer. The air and water side heat transfers need to 
be equal or else there is an energy imbalance across the coil.
Best,
 David
 

Fred Betz wrote:
>
> All,
>
>  
>
> There appears to be a bug in the Type 670-1 heating coil.
>
>  
>
> I set the effectiveness of the coil to 0.70, but the air and water 
> side heat transfer rates are approximately equal.
>
>  
>
> Anyone have a fix?
>
>  
>
> Fred
>
>  
>
>  
>
> *Fred Betz**  *PhD., LEED AP
> Sustainable Systems Analyst
>
> 	
>
>  
>
> 	
>
> *AEI* | AFFILIATED ENGINEERS, INC.  
> 5802 Research Park Blvd. | Madison, WI  53719
>
> P: 608.236.1175 | F: 608.238.2614  
> fbetz at aeieng.com <mailto:fbetz at aeieng.com>  |  *www.aeieng.com 
> <http://www.aeieng.com/>*  
>
>  
>
>  
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>   

-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100329/2d8db820/attachment-0005.htm>


More information about the TRNSYS-users mailing list