[TRNSYS-users] Type 34 and type 67 combination problem

Adrien JEZEQUEL - ITF a.jezequel at itf.biz
Wed Mar 24 07:26:01 PDT 2010


Dear Fredericks

In your model, you haven't define all of your wingwall and overhang in 
Type34.
You just define your receiver dimensions, without describing overhang or 
wingwall geometry (you just define an oerhang in "1_OVERHANG_ZONE_IV_VOOR")
If you observe the results of your "schaduwTOT" with a viewer, you see 
that when overhang and wingwall are not defined in type34, shading 
factors you calculate are negatives.

Best regards

------------------------------------------------------------------------
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>

	Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
	62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
	+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz

/Afin de contribuer au respect de l'environnement, merci de n'imprimer 
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/

Le 24/03/2010 13:29, frederik.holderbeke at kahosl.be a écrit :
>
> Hello,
>
> In order to calculate the shading of a nearby building in combination 
> with the effects of an overhang we used the type 67 and type 34 in 
> simulation studio.
> We made all the connections discribed in: 
> http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/connecting34_67.pdf
> However we want to use the solar shading fraction on the reciever to 
> connect with the building file type 56 as an external shading factor 
> on a window.
> For this, we always get a negative number.
>
> In attachments you will find our .bui, .tpf and type 67 external file
>
> Greatings,
> Frederik
>
>
> ---------------------------------------------------------------------------------------
> Orange vous informe que cet e-mail a été contrôlé par l'anti-virus mail.
> Aucun virus connu à ce jour par nos services n'a été détecté.
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100324/7cbbd75f/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_signature.jpg
Type: image/jpeg
Size: 2884 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100324/7cbbd75f/attachment-0005.jpg>


More information about the TRNSYS-users mailing list