Héloïse,
I don't think Type34 is going to work for non-vertical windows; it
contains an analytical solution for the view factor between a vertical
surface, the horizontal ground and a horizontal overhang. In the case of
a non horizontal overhang, we take the horizontal projection of the
overhang. That view factor calculation isn't going to be correct for a
non-vertical surface. You might consider using Type67 which allows you
to define a shading mask but that component calculates shading from the
center of glass and so ignores the effect of the window's slope.
Best,
David
Heloise PELEN wrote:
>
> Dear TRNSYS users,
>
>
>
> I am currently working on a project which involves non-orthogonal
> windows, shaded by horizontal overhangs. I'd like to use type 34 to
> model these overhangs. My windows have different slopes, from 30° to
> 80° with the horizontal direction.
>
>
>
> 1. Type 109, from which the radiation inputs of type 34 come, uses
> the slope of my tilted windows to compute the beam radiation and the
> incident angle of direct radiation on this non-orthogonal surface. Is
> it enough to tell type 34 that my windows are not orthogonal ? Indeed,
> the description of the 1^st parameter of type 34 reads: "Type34
> assumes a vertical orientation for the window." The problem is that,
> my window not being vertical, an overhang doesn't have the same impact
> than if the window was vertical, since the window is closer to the
> sun's zenith angle.
>
>
>
> 2. What length of overhang projection and overhang gap should I
> consider ? Mark Duffy's answer on Fri Dec 11^th 2009 suggests that we
> should take the horizontal distance for the overhang projection, but
> is this right even in this case, with a non vertical window ? Should I
> take instead the distance in the orthogonal direction from the window
> to the end of the projection ?
>
>
>
> Thanks for your help.
>
>
>
> Best regards,
>
>
>
> *Héloïse Pelen*
>
> *ETAMINE*
>
> *etamine_mail*
>
>
>
> heloise.pelen at etamine.coop <mailto:heloise.pelen at etamine.coop>
>
> 75 rue de la Villette - 69003 Lyon
>
> Std : 04 37 45 34 20 / Fax : 04 37 45 41 38
>
> Ld : 04 37 45 34 13
>
>
>
> Visitez notre nouveau site web : www.etamine.coop !
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100312/b2b7af8f/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 5948 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100312/b2b7af8f/attachment-0005.png>
More information about the TRNSYS-users
mailing list