[TRNSYS-users] Heating Cooling Power
David Bradley
bradley at tess-inc.com
Fri Mar 12 08:40:16 PST 2010
Roberto,
I would not use the heating type manager in TRNBuild; what that does
is to impose a set point temperature on the building and have Type56
calculate the required load that should be met by the heat pump. The
heat pump, however, does not take a load input. It takes inlet
conditions and calculates outlet conditions. Instead, I would recommend
that you define a ventilation stream in your Type56 zone (using the
ventilation type manager in TRNBuild) with temperature, flow rate, and
RH as INPUTS. Then pass the heat pump outlet conditions to the new
Type56 inputs. You'll also need to define a thermostat that watches the
zone temperature and turns the heat pump on and off.
There is a tutorial that will give you some hints as to how to do this.
It can be found at:
http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex.htm
"Temperature Level Control from Energy Rate Control
<http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tlc_tutorial.pdf>,
using the TRNSYS 16 Restaurant Example"
Best,
David
caria.roberto at tiscali.it wrote:
> dear trnsys users,
> I have simulated an heat pump and now I'd like to connect it with
> Trnbuild to understand if its power is acceptable to heating and
> cooling load: set point temperature of zone is 20°C for winter and 26°C
> for summer, how can I do it? Perhaps I just have to link
> heating/cooling power obtained from heat pump with limited mode on
> "Heating Type Manager" and set temperature on 20/26°C or is there a
> specific type? I use only standard library.
> Thanks
> Roberto
>
>
>
> Presentaci un amico! Invita i tuoi amici a scoprire i servizi Tiscali: per ogni amico che attiverà un servizio Tiscali, potrai avere 30 euro di sconto e lo stesso sconto di 30 euro verrà poi offerto al tuo amico. Scopri come! http://abbonati.tiscali.it/presentaci_un_amico/?WT.mc_id=01fw
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100312/e78efb53/attachment-0005.htm>
More information about the TRNSYS-users
mailing list