[TRNSYS-users] Type 107 - description of used values

David Bradley bradley at tess-inc.com
Thu Mar 11 09:10:24 PST 2010


Timo,
  You are right, that documentation is confusing and I think one of the 
equations is incorrect...

  To clarify: what the documentation refers to as the "fraction of 
design load" is the energy that has to be removed from the water stream 
(ie the current load) divided by the machine's rated  capacity. 
Essentially it is the part load ratio at which the machine has to 
operate. However, based on the current entering cooling water and hot 
water temperatures, the machine's entire rated capacity may not 
currently be available. So, the calculated fraction of design load and 
the entering water conditions are sent to the data file and the data 
file returns what is calls the "fraction of the rated capacity" that is 
currently available. The value is returned as a fraction, not as a 
capacity; thus "fraction of rated capacity." So basically, the "fraction 
of design load" is an input to the data file based on only on rated 
capacity and current load and the "fraction of rated capacity" is 
returned, taking into account the current entering water conditions.

  In the source code, the returned fraction of rated capacity that is 
returned from the data file is multiplied by the machine's full-load 
capacity to determine nominal capacity. The equation that I think is 
incorrect in the documentation is Eq. 5.3-95. There should only be one 
multiplier on Capacity_Rated, not two and that multiplier is the one 
returned from the data file (whatever you want to call it).
Best,
 David


Timo Sengewald wrote:
>
> Hello!
>
>  
>
> I try to set up a Type 107 absorption chiller by using manufacturer's 
> data but do not understand the difference between the "Fraction of 
> Design Load" and the "fraction of rated capacity" as described in the 
> mathematical reference. I understand the meaning of the fraction of 
> design load. But what is meant by the "fraction of rated capacity" 
> which is returned by the data file? Both terms mean the same to me.
>
>  
>
> Is somebody able to describe the difference in other words than used 
> in the manual?
>
>  
>
> Best regards
>
>  
>
> Timo
>
>  
>
>  
>
>
>
> Mit freundlichen Grüßen
>
> BLS Energieplan GmbH
> i. A. Timo Sengewald
>
> Elsenstraße 106
> D-12435 Berlin
> Tel.: +49 30 53 32 81-0
> Fax: +49 30 53 32 81-40
> ____________________________________________________
> BLS Energieplan GmbH
> Sitz der Gesellschaft: Berlin
> Geschäftsführer: Christoph Lange, Wolfgang Sturm
> Registergericht: Amtsgericht Berlin-Charlottenburg, HRB-Nr. 32021
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>   

-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100311/8eea24c6/attachment-0005.htm>


More information about the TRNSYS-users mailing list