[TRNSYS-users] Heating Coil: Type 670-1 bug
David Bradley
bradley at tess-inc.com
Mon Mar 29 14:17:30 PDT 2010
Fred,
I think you might be confusing efficiency and effectiveness.
Effectiveness is actual energy transfer divided by maximum theoretically
possible energy transfer. The air and water side heat transfers need to
be equal or else there is an energy imbalance across the coil.
Best,
David
Fred Betz wrote:
>
> All,
>
>
>
> There appears to be a bug in the Type 670-1 heating coil.
>
>
>
> I set the effectiveness of the coil to 0.70, but the air and water
> side heat transfer rates are approximately equal.
>
>
>
> Anyone have a fix?
>
>
>
> Fred
>
>
>
>
>