[TRNSYS-users] Multiple Wingwalls
David Bradley
bradley at tess-inc.com
Tue Mar 23 08:28:29 PDT 2010
Mohannad,
If I am understanding your configuration correctly, you have a large
west facing facade that has vertical fins projecting perpendicularly
every 2 meters? If this is the case, you can think of the facade as a
series of 2m sections all of which are identical. So you could define a
Type34 for the repeating section: width 2m, height 3m each with a left
and a right wingwall that projects 1.8m. Type34 calculates solar
radiation per unit area on the facade so you can then apply its
calculated result to the entire 18m x 3m facade. If you wanted to be a
little more rigorous, you could define two Type34s, one for the opaque
part of each 2m wall section and one for the transparent part. If you
are using Type56, you would then have to define your windows in the
"additional windows" category so that they can have a different
ORIENTATION name than does the wall. Recall that all an ORIENTATION
means in TRNBuild / Type56 is that a certain amount of radiation per
unit area falls on all surfaces having that ORIENTATION.
Best,
David
Mohannad Bayoumi wrote:
> Dear all,
>
> I am trying to model multiple vertical wingwalls on the west facade
> (one zone) h 3 x w 18 m. Dimensions of the transparent part h 1.5 x w
> 18 m.
>
> The problem is that type 34 does not ask for the amount of elements,
> as if it would consider the whole facade one window.
>
> Could more than 1 wingwall element assigned to the facade. For
> instance every 2 meters with a projection of 1.8 m.
>
> Thanks
> --
> Mohannad Bayoumi
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100323/d12f9efe/attachment-0001.htm>
More information about the TRNSYS-users
mailing list