[TRNSYS-users] Blinds
Adrien JEZEQUEL - ITF
a.jezequel at itf.biz
Tue Jun 22 07:18:50 PDT 2010
Dear Julie,
I suggest you to put an equation tool outside of Type56. In that
equation tool, ESHAD (the ratio of non transparent area of the shading
device to the whole glazing area, as defined in TRNBUILD) will be
calculated depending on blinds position.
If you consider that :
* GWINDOW = solar shading factor of window only, which is constant
(60% for example, which means that 60% of solar radiation goes
through the window)
* FS = solar shading factor of your system Window + Shadings.
FS depends on blinds use,
o if blinds are used, FS = 0.2 (for example)
o if not, FS = GWINDOW
In that way, FS is calculated as the product between :
* the amount of solar energy which pass through external shading
device when they're used => (1-ESHAD)
o ESHAD = 0 means no shading
o ESHAD = 1 means zero transmission
* and window solar shading factor (GWINDOW)
o *FS = GWINDOW.(1-ESHAD)* (1)
Regarding (1)* *
*ESHAD = (1- FS/GWINDOW**) *(2)
No you have a relation between ESHAD, FS and Window G-Value :
* When blinds are up, solar radiation are only blocked by the window
solar shading factor => FS = GWINDOW and ESHAD = 0.
* When blinds are down, solar radiation are blocked by window *and*
external shadings => FS = 0.2 (for the whole system in that
example), ESHAD = (1-0.2/0.6) = 0.667 that means that 66.67% non
transparent area of the shading device to the whole glazing area)
Regarding (1) FS = 0.5*(1-0.0.667) = 0.5*0.4 = 0.2 which is the
total shading factor you want.
Best
------------------------------------------------------------------------
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz
/Afin de contribuer au respect de l'environnement, merci de n'imprimer
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/
Le 22/06/2010 14:04, Julie Lestrade a écrit :
> Dear TRNSYS users,
>
> I was wondering about blinds in front of windows and how to take them
> into account.
> In my case, they external blinds. They're up at certain time and down
> at other (depending on radiation on the wall, time of day, ...).
>
> Should I take account of them in Type 56 ? on the windows considered
> with 'external shading factor' (that would be convenient since i can
> use a schedule) ? If yes, I would like to have a total solar factor
> for the window of 0.2 when the blind is down. Does that mean I should
> put a shading factor 0.8 ? or is it more complicated than that ?
>
> Thank you for your answers
>
> Julie
>
>
> ---------------------------------------------------------------------------------------
> Orange vous informe que cet e-mail a été contrôlé par l'anti-virus mail.
> Aucun virus connu à ce jour par nos services n'a été détecté.
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100622/0e7087fe/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_signature.jpg
Type: image/jpeg
Size: 2884 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100622/0e7087fe/attachment-0005.jpg>
More information about the TRNSYS-users
mailing list