[TRNSYS-users] help
David Bradley
bradley at tess-inc.com
Tue Jun 29 12:17:03 PDT 2010
Imen,
I assume you are using TRNSYS 16 or 17. If so, you can use the PID
controller (Type23). Please pay particular attention to the mode setting
(parameter 1) and if you use mode zero, set a small time step and make
sure that you have some thermal capacitance in your system. Most heat
exchanger models ignore thermal capacitance and compute a steady state
solution. Without sufficient capacitance in the system (in the form of
pipes and tanks), it might be very hard to control the outlet
temperature of your heat exchanger.
Best,
David
On 6/27/2010 10:17, imen chraief wrote:
>
> Dear
>
> I used a heat exchanger (air /water) the hot side fluid is water
> extracted from a storage tank connected to solar thermal collector and
> the cold side fluid is an air.
>
> Hot side inlet temperature and cold side inlet temperature are known
> and are in function of time, and the cold side outlet temperature is
> imposed 68°C; how achieve a constant temperature with this model?
>
> Please help me the fastest possible it is very urgent; thank you and apologize for this bad English text
> Best regards
> imen
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100629/49dc1c30/attachment-0001.htm>
More information about the TRNSYS-users
mailing list