[TRNSYS-users] some questions about capillary tube system
David Bradley
bradley at tess-inc.com
Thu Jun 17 09:36:26 PDT 2010
Chen Shuai,
I believe that "segments" in this case refers to the TRNBuild / Type56
autosegmentation feature. When you have an active layer whose specific
flow rate is low (below 13kg/h.m2) you cannot treat the entire floor as
a single entity but you have to break it up into a series of segments
that are all in series (one feeds into the next). This is all done
automatically for you in TRNBuild; specify the specific flow rate that
you want to use in your floor and then press the "do" autosegmentation
button. The floor will be broken up into as many segments as needed in
order to achieve your flow rate.
Best,
David
On 6/16/2010 11:23, ahaxe chen wrote:
> Hi, all:
> Such a passage about capillary tube system says on page
> 6-31:"Unfortunately, 2 segments in series like for the ordinary piping
> system are insufficient: Depending on the entered data up to 8
> segments are required." Does this "segment" mean "layer" which
> mentioned earlier. And what is the basis to say "up to 8 segments "?
> What segments are included in the series?
> thank you !
> best regards
> Chen Shuai from China
> 2010.6.17
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100617/058f45b2/attachment-0001.htm>
More information about the TRNSYS-users
mailing list