[TRNSYS-users] Air-water heat pump
David Bradley
bradley at tess-inc.com
Wed Jul 7 08:27:50 PDT 2010
Mavi,
I faced this same situation at one point and was able to use Type505
by turning it around backwards. Fundamentally, when Type505 refers to
"heating," it is heating the air stream and cooling the water stream.
When it is "cooling" it is cooling the air and heating the water stream.
In your case, "heating" means heating the water and cooling the air. So
if you treat Type505's "cooling" control signal as though it were your
"heating" control signal, it should work fine.
I believe that in upcoming Tess Libraries 17, there is a specific
component for what you are trying to do but I am not aware of its status
at the moment.
Best,
david
On 7/7/2010 07:06, Mavi Cambronero Vázquez wrote:
> Hi all!
> I´m looking for a typical air-water heat pump. I have HVAC library
> from TESS but the type that is called water-source heat pump is not
> what I need. The scheme is the same but the fluid stream and the air
> stream air in opposite places, that is, if I want to simulate a
> conventional heat pump in order to cool the air inside a building what
> I need to cool is the liquid stream that would be indoor. In that
> case, the air flow would be outdoor. Type 505 is what Ì´d need but
> exchanging both streams.
> I don´t know if I explained well my problem. Does anybody know the
> correct type to simulate an air-water heat pump, with the water stream
> indoor?
> Thanks in advance.
> Best,
> Mavi
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100707/64877b30/attachment-0005.htm>
More information about the TRNSYS-users
mailing list