[TRNSYS-users] Beam and diffuse radiation from global radiation
    Laia Cases - iMat 
    lcases at imat.cat
       
    Wed Jul 14 01:41:25 PDT 2010
    
    
  
Benoit,
if you have also measured ambient temperature and relative humidity, you 
can use type16c  (Total horitzontal, temperature and  humidity known)
Laia
En/na Sébastien THOMAS ha escrit:
>
> Dear Benoît,
>
>  
>
> You can use Type 16a to achieve the computation of beam and diffuse 
> radiation based on total horizontal radiation only.
>
>  
>
> Be careful about the time (local or not) of your measured data.
>
>  
>
> On the picture is mentioned the path to find Type 16a !
>
>  
>
>  
>
> Regards
>
>  
>
> /Sébastien Thomas
> Assistant - Doctorant
>
> Université de Liège
> Département Sciences et Gestion de l'Environnement
> Equipe BEMS   - Building Energy Monitoring and Simulation -
> 185, Avenue de Longwy
> B-6700 ARLON
>
> / [BEMS]
> /  Tel: 32-(0)63-230 982
>   Fax: 32-(0)63 230 800
>   email: sebastien.thomas at ulg.ac.be <mailto:sebastien.thomas at ulg.ac.be>
>   WEB: http://www.bems.ulg.ac.be ///
>
>  
>
>  
>
>  
>
> ------------------------------------------------------------------------
>
> *De :* COGNE Benoit (Axima Seitha) 
> [mailto:benoit.cogne at aximaseitha-gdfsuez.com]
> *Envoyé :* mardi 13 juillet 2010 15:15
> *À :* trnsys-users at cae.wisc.edu
> *Objet :* [TRNSYS-users] Beam and diffuse radiation from global radiation
>
>  
>
> Dear all,
>
>  
>
> I am getting weather measurements with the global radiation on the 
> horizontal only.
>
> Is there a way (correlation) to split it in beam and diffuse radiation ?
>
>  
>
> Thanks in advance for your help
>
>  
>
> *Benoît COGNE* 
> Développement Efficacité Energétique 
> ___________________________________________________
>
>
> *
> **Direction Commerciale*** 
> 46 Boulevard de la Prairie au Duc
> BP 40119 - 44201 Nantes Cedex 02 
> Tel. 02 40 41 00 81
> mail: benoit.cogne at aximaseitha-gdfsuez.com 
> <mailto:benoit.cogne at aximaseitha-gdfsuez.com>_
> _www.aximaseitha-gdfsuez.com
>
> P *Pensez à l'environnement avant d'imprimer ce message*
>
>  
>
>  
>  
>  
> GDF SUEZ Mail Disclaimer: http://www.gdfsuez.com/disclaimer/disclaimer-fr.html
>  
>  
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>   
-- 
	*Laia Cases*
Unitat de Condicionament Tèrmic
*iMat - Centre Tecnològic de la Construcció
lcases at imat.cat <mailto:lcases at imat.cat>
www.imat.cat <http://www.imat.cat/>*
	Wellington 23  ·   E-08018 Barcelona
T +34 93 553 97 95
F +34 93 553 97 96
Imprimiu aquest document només si és necessari
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100714/5013f0fa/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 25343 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100714/5013f0fa/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2650 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100714/5013f0fa/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3512 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100714/5013f0fa/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: imat.jpg
Type: image/jpeg
Size: 30755 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100714/5013f0fa/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: tecnio.jpg
Type: image/jpeg
Size: 27188 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100714/5013f0fa/attachment-0001.jpg>
    
    
More information about the TRNSYS-users
mailing list