Mariana,
Do any of your walls have the "automatic heat transfer coefficient"
calculation option turned on? If so, try to (temporarily) set them all
to constant coefficients. TRNBuild/Type56 doesn't allow that mode to be
used on the outside surface of an EXTERNAL wall. Years ago, I did have
the problem where I had all walls set with constant heat transfer
coefficients and still got that error but the bug was corrected in a
quite early release of Trnsys16 (2005 at the latest).
Best,
David
On 7/6/2010 16:05, ghetu mariana wrote:
>
> Hello,
>
> Has anyone had this kind of error message?
>
> "Error in automatic heat transfer calculation for surface 399 or its
> adjacent surface!: Automatic heat transfer calculation is only allowed
> on surfaces within a zone. Please check building input file."
>
> Surface 399 is adjacent and the wall time has the front convective
> heat transfer coefficient set to 11 kJ/h,m2K and the back to 12
> kJ/h,m2K. It's supposed to be working this way but I have the same
> error message.
>
> Thanks in advance,
>
>
> Mariana GHETU
> ------------------------------------------------------------------------
> *From:* "trnsys-users-request at cae.wisc.edu"
> <trnsys-users-request at cae.wisc.edu>
> *To:* trnsys-users at cae.wisc.edu
> *Sent:* Tue, 6 July, 2010 20:20:51
> *Subject:* TRNSYS-users Digest, Vol 67, Issue 12
>
> Note: Forwarded message is attached.
>
> Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>
> To subscribe or unsubscribe via the World Wide Web, visit
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
> <mailto:trnsys-users-request at cae.wisc.edu>
>
> You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu <mailto:trnsys-users-owner at cae.wisc.edu>
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
> Today's Topics:
>
> 1. Re: windows in Trnsys (David Bradley)
> 2. Re: type 557 run time error 6 overflow (David Bradley)
> 3. Re: problem (David Bradley)
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100706/49a5f645/attachment.htm>
More information about the TRNSYS-users
mailing list