Dear Kent,

To model dehumidifcation you need to use the cooling manager, and not 
the heating one.
By setting 100% in heating (and thus in humidification) you force TRnsys 
to add humidity to your local.

If you want 60% (no more, no less) during occupation, you have to set 
the things like this:
inoccupation:
heating: X°C, 0%
cooling: X°C, 100%

Occupation:
heating: Y°C, 60%
cooling: Y°C, 60%

Happy new year to every TRNSYS users.
Regards.