[TRNSYS-users] Type 107 Absorption Chiller in Solar Cooling Model
#GOH KIM LAI DENNIS#
Z060113 at ntu.edu.sg
Mon Jan 25 00:08:59 PST 2010
Dear TRNSYS users,
I'm wanting to simulate a Type 107 absorption chiller.
I am wondering if the example external datafile provided in C:\Program Files\Trnsys16_1\Examples\Data Files\Type107-HotWaterFiredAbsorptionChiller.dat can support the parameters I used.
Parameters used:
Rated Capacity: 90000kJ/hr or 25kW
Rated COP: 0.7
m chilled water: 100kg/hr
Tchw,in: 12.22C
Tchw,out: 6.667C
ffullcapacity: 1.0
Thw,in: 84.0C
>From the Mathematical Reference, I calculated the following values:
Qremove = 2326.707kJ/hr
fdesign load = 0.025
fnominalcapacity = 0.7898
Capacity = 69444kJ/hr or 19.3kW
fdesignenergyinput = 0.03108
Qhotwater = 3996kJ/hr
Thw,out = 83.04C
Is the example datafile suitable for my model Type 107?
Does anyone have a datafile that simulates absorption chillers in the range of 20-30kW?
Or how can I edit a datafile to suit an absorption chiller of 30kW?
Thanks in advance!
Dennis Goh
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100125/9e61d104/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Solar Absorption Cooling_2.tpf
Type: application/octet-stream
Size: 243836 bytes
Desc: Solar Absorption Cooling_2.tpf
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100125/9e61d104/attachment-0001.obj>
More information about the TRNSYS-users
mailing list