[TRNSYS-users] Type 534 Illegal parameter
Matteo DF
deframat at gmail.com
Thu Feb 4 01:04:42 PST 2010
David,
thanks for your reply... I think you've hit the problem! I will perform some
checks to be sure that the heat exchanger isn't larger in volume than the
tank itself... Probably in type60 there wasn't such a check becouse I'm
trying to replace them using the same parameters...
Have a good day,
Matteo
On 3 February 2010 18:47, David Bradley <bradley at tess-inc.com> wrote:
> Matteo,
> If you're getting an error having to do with an HX node and also with
> parameter 2 then what might be happening is that the volume of your heat
> exchanger (or heat exchangers) is larger than the volume of your tank. We
> are aware of the problem of matching bad parameters to values in the data
> file (or to the plugin) and we're working on a solution to it.
> Best,
> David
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100204/7853b7f4/attachment-0005.htm>
More information about the TRNSYS-users
mailing list