Mariëlle,
In TRNSYS 16, the absorption for solar radiation can be set using the
wall type manager. The emissivity for the wall surface, however is
hardcoded inside Type56. You are correct that Type56 uses a star network
for radiation exchange. All surfaces radiate to the airnode and the
airnode radiates to all surfaces. There are no view factors. The one
control you have is the geosurf factor with which you can specify the
fraction of longwave radiation entering a zone that falls on a
particualr surface.
In TRNSYS 17 you can define "radiation zones" which DO have view
factors provided that you have used the Trnsys3D plugin for Google
SketchUp to generate those view factors for your building's geometry.
You can also adjust the emissivity of the walls within TRNBuild.
I am not as sure what to suggest for setting the temperature of the
wall. Inside (and outside) surface temperatures are calculated as part
of the zone energy balance. You might be able to use a thermostat and
the "wall gain" feature to control the inside surface temperature of
your warm wall.
Best,
David
Mariëlle Nuchelmans wrote:
>
> Hello,
>
>
>
> I'm trying to understand how trnsys deals with long-wave radiation. I
> know that trnsys calculates it with the star network method from Seem
> (adjusted by Koschenz in 1997). I looked at the method and I wonder
> how the absorption factor between surfaces is determined. Seem refers
> to Gebhart, but this method uses view-factors and trnsys doesn't know
> them. So how does trnsys determine this absorption factor?
>
>
>
> I also wonder if it is possible to adjust (or make variable) the mean
> average wall temperature (used to linearize the long-wave radiation
> exchange between surfaces between zones). In my project I have one
> wall which probably is a lot warmer than the other walls.
>
>
>
> Met vriendelijke groet,
>
>
>
> Mariëlle Nuchelmans
>
> ------------------------------------------------------------------------
>
> Cauberg-Huygen Raadgevende Ingenieurs BV
> *M. Nuchelmans-van Wanum* | Assistent Projectleider | Cauberg-Huygen
> Raadgevende Ingenieurs BV (Maastricht, KvK 14623897)
> Pettelaarpark 101 | 5216 PR | Postbus 638 | 5201 AP | 's-Hertogenbosch
> *T* 073-7517936 | *F* 073-7517901 | *M* -
> m.nuchelmans at chri.nl <mailto:m.nuchelmans at chri.nl> | www.chri.nl
> <http://www.chri.nl> | disclaimer <http://www.chri.nl/emaildisclaimer>
>
> Denk aan het milieu en print deze email alleen als het noodzakelijk is.
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100210/31dfe511/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 3734 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100210/31dfe511/attachment-0001.gif>
More information about the TRNSYS-users
mailing list