[TRNSYS-users] Type 534 Illegal parameter
David Bradley
bradley at tess-inc.com
Wed Feb 3 09:47:38 PST 2010
Matteo,
If you're getting an error having to do with an HX node and also with
parameter 2 then what might be happening is that the volume of your heat
exchanger (or heat exchangers) is larger than the volume of your tank.
We are aware of the problem of matching bad parameters to values in the
data file (or to the plugin) and we're working on a solution to it.
Best,
David
Matteo DF wrote:
> Hi everybody,
> as suggested in some previous mails, I'm starting using type 534
> instead of type60 (because of the known bug which don't let use more
> than one in a model).
> Anyway things are not very simple: I sometimes get some 103 errors, in
> the description there's explained that some parameter of the tank is
> illegal... I've had some problems with parameter 44 (which i
> discovered it was HX node related). This time I'm getting errors with
> parameter 2, which I think it's about the number of nodes or the
> volume... Possible?
>
> Anyway, the question is: how can I match the parameter number (given
> by the error 103) and the exact parameter in the tank?
>
> If you have any other suggestion about modeling a tank with type 534
> it would be really apprechated.
>
> PS: I'm using the plugin, of course...
>
> Thanks,
> Matteo.
>
> --
> La scoperta è vedere ciò che tutti hanno sempre visto e
> pensare ciò che nessuno ha mai pensato.
> (Albert Szent-Gyorgyi, scopritore della vitamina C e premio Nobel)
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100203/187bd9a5/attachment-0001.htm>
More information about the TRNSYS-users
mailing list