[TRNSYS-users] zone air temperature (NTYPE 1: TAIR)
王洋
wanghongyang1767 at gmail.com
Fri Dec 17 05:22:14 PST 2010
Dear all,
I have a question about room air temperature: NTYPE 1: TAIR. As we
know, there are different room air temperature in different height of one
room. Besides that, the wall, the floor and roof temperature of the room
are also not the same. Please tell me what's meaning of NTYPE 1: TAIR?
Where is This AIRNODE? How to define This AIRNODE?
PLUS: to Operative(operation) temperature of room: How to define
it? What' meaning is Operative(operation)temperature of room? What's
difference of Operative(operation) temperature of room and NTYPE 1: TAIR?
Many thanks!
Br.
wang
2010/12/17 <trnsys-users-request at cae.wisc.edu>
> Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
> 1. Re: Type 56 (David BRADLEY)
> 2. Re: Psychrometrics (David BRADLEY)
> 3. Re : Re: Psychrometrics (Jérôme Deroche)
> 4. error when opening sketchup (Annie Marston)
>
>
> ---------- 已转发邮件 ----------
> From: David BRADLEY <d.bradley at tess-inc.com>
> To: Abduljalil Ali Al-Abidi <abo_anas4 at yahoo.com>
> Date: Thu, 16 Dec 2010 12:47:43 -0600
> Subject: Re: [TRNSYS-users] Type 56
> Abduljalil,
> In order to change the wall layers, open TRNBuild and open your building
> description file (*.bui or *.b17). Select Typemanager: Walls from the menus
> at the top of the screen. Select the appropriate wall from the drop-down
> list. Double click on a layer in order to change its thickness.
> Best,
> David
>
>
> On 12/16/2010 03:26, Abduljalil Ali Al-Abidi wrote:
>
> Dear Trnsys user
> I am a new trnsys user and I want to change the thickness of the wall
> insulation in the tape 56 ( multi-zone building ). Is it possible to change
> this thickness in this type ex. for insulation = 5 cm to 20 cm step 5cm.
> I would like to study the effect of insulation thick to the performance of
> the system
> best regards
>
>
> _______________________________________________
> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475d.bradley at tess-inc.com
> http://www.tess-inc.comhttp://www.trnsys.com
>
>
>
> ---------- 已转发邮件 ----------
> From: David BRADLEY <d.bradley at tess-inc.com>
> To: "Jérôme Deroche" <deroche.jerome at cedre-sophia.com>
> Date: Thu, 16 Dec 2010 12:50:55 -0600
> Subject: Re: [TRNSYS-users] Psychrometrics
> Jérôme,
> What is most likely happening is that at a pressure of 1atm, your
> combination of the dry bulb temperature and the absolute humidity ratio are
> on the wrong side of the saturation line. Since that is physically
> impossible, the psychometric routine keeps your dry bulb temperature and
> resets the absolute humidity ratio to the value it would be if the relative
> humidity were 100%.
> Best,
> David
>
>
> On 12/16/2010 04:21, wrote:
>
> Hello,
> i'm using a psychrometrics type with dry bulb temperature and absolute
> humidity ratio in inputs. Pressure input is set to 1 atm.
>
> I have noticed that sometimes there is a difference between the input
> humidity ratio and the output humidity ratio. The difference ratio is about
> 1 to 12%.
>
> Could someone explain to me why this difference happens?
>
> Thank you
>
> Jérôme DEROCHE
> Ingénieur d'études
>
> CEDRE
>
> Tel: 04 92 96 03 77
> Port: 06 25 11 21 93
> Ophira 1, 1 place Bermond
> 06560 SOPHIA-ANTIPOLIS
>
>
> _______________________________________________
> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475d.bradley at tess-inc.com
> http://www.tess-inc.comhttp://www.trnsys.com
>
>
>
> ---------- 已转发邮件 ----------
> From: "Jérôme Deroche" <deroche.jerome at cedre-sophia.com>
> To: David BRADLEY <d.bradley at tess-inc.com>
> Date: Fri, 17 Dec 2010 05:08:17 -0500 (EST)
> Subject: [TRNSYS-users] Re : Re: Psychrometrics
> Your answers are right.
> Thank you very much
>
>
>
> Jérôme DEROCHE
> Ingénieur d'études
>
> CEDRE
>
> Tel: 04 92 96 03 77
> Port: 06 25 11 21 93
> Ophira 1, 1 place Bermond
> 06560 SOPHIA-ANTIPOLIS
>
>
> Message original Re : Re: [TRNSYS-users] Psychrometrics*De : *David
> BRADLEY <d.bradley at tess-inc.com>
> *A : *Jérôme Deroche <deroche.jerome at cedre-sophia.com>
> *Date* : 2010-12-16 19:51:05
>
> Jérôme,
> What is most likely happening is that at a pressure of 1atm, your
> combination of the dry bulb temperature and the absolute humidity ratio are
> on the wrong side of the saturation line. Since that is physically
> impossible, the psychometric routine keeps your dry bulb temperature and
> resets the absolute humidity ratio to the value it would be if the relative
> humidity were 100%.
> Best,
> David
>
>
> On 12/16/2010 04:21, wrote:
>
> Hello,
> i'm using a psychrometrics type with dry bulb temperature and absolute
> humidity ratio in inputs. Pressure input is set to 1 atm.
>
> I have noticed that sometimes there is a difference between the input
> humidity ratio and the output humidity ratio. The difference ratio is about
> 1 to 12%.
>
> Could someone explain to me why this difference happens?
>
> Thank you
>
> Jérôme DEROCHE
> Ingénieur d'études
>
> CEDRE
>
> Tel: 04 92 96 03 77
> Port: 06 25 11 21 93
> Ophira 1, 1 place Bermond
> 06560 SOPHIA-ANTIPOLIS
>
>
> _______________________________________________
> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475d.bradley at tess-inc.com
> http://www.tess-inc.comhttp://www.trnsys.com
>
>
>
> ---------- 已转发邮件 ----------
> From: Annie Marston <A.Marston at eb-engineers.com>
> To: "trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>
> Date: Thu, 16 Dec 2010 14:30:35 +0000
> Subject: [TRNSYS-users] error when opening sketchup
>
> Hi,
>
>
>
> I am using the TRNSYS 3d plugin for SketchUp V7. I have v8 but the plugin
> doesn’t seem to attach to v8 (is this correct? Is there a plugin for v8).
> Whenever I open sketch up I get the following error:
>
> Sorry… the plugin has encountered an error. This error may cause
> unpredictable behavior in the plugin continue this session with caution! It
> would probably be a good idea to exit SketchUp and start again.
> (unfortunately this happens everytime I open sketchup)
>
>
>
> For help please contact…
>
>
>
> Error:
>
> NameError
>
> Wrong constant name jectinfoInterface
>
>
>
> Backtrace:
>
> C:/Program Files (x86)/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in `const_get'
>
> C:/Program Files (x86)/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in `restore_state'
>
> C:/Program Files (x86)/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/DialogManager.rb:31:in `initialize'
>
> C:/Program Files (x86)/Google/Google SketchUp
> 7/Plugins/Trnsys3d/lib/AsynchProc.rb:13:in `call'
>
>
>
>
>
> My version of the plugin is 1.0.5.362
>
>
>
> Can you help
>
>
>
> Thanks
>
> Annie
>
>
>
> *Dr. A. Marston, Ph.D. LEED® AP*
>
> *Building Performance Analyst*
>
>
>
> *Ebert & Baumann Consulting Engineers, Inc.*
>
> *An Enterprise of the Ebert-Consulting Group***
>
>
>
> 734 15th Street, NW
>
> Suite 1000
>
> Washington, D.C. 20005, USA
>
> *Tel +1.202.608.1334***
>
> *Fax +1.202.544.1434*
>
> * *
>
> *a.marston at eb-engineers.com*
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20101217/48d75c1e/attachment-0005.htm>
More information about the TRNSYS-users
mailing list