[TRNSYS-users] heat exchangere
David BRADLEY
d.bradley at tess-inc.com
Tue Dec 14 13:56:15 PST 2010
Elly,
If you have the TESS HVAC library, there are a number of heat
exchangers with controlled outlet temperature models in there. If not
then you will need to use a variable speed pump (Type3) , the heat
exchanger, and (most likely) a PID controller (Type23).
Best,
David
On 12/13/2010 15:24, e.nicolazzi at libero.it wrote:
>
> Dear Transys-user,
>
> I'm simulating, with trnsys 16, a plate heat exchanger for district heating
> substation. I'm using type 5b, is it correct?
> There's a control unit that in function of external temperature and the hot-
> side outlet temperature (secondary pipe) open or close (%) the valve in the hot-
> side inlet temperature (primary pipe).
> Can someone tell me how can i model a control unit? which types can i use?
>
> Thanks in advance,
> Elly
>
>