[TRNSYS-users] Problem to model shading mask with Trnsys 3D
    Matt Duffy 
    duffy at tess-inc.com
       
    Wed Aug 25 04:27:48 PDT 2010
    
    
  
Dear Vincent,
After importing your *.idf into trnbuild, you need to generate the shading matrix, *.shm, from the menu (Generate -> Shading/Insolation Matrix)
Best regards,
Matt Duffy
Thermal Energy Systems Specialists
Sent from my mobile wireless device. Please excuse any typos.
On Aug 25, 2010, at 4:40 AM, "vincent.coste at amoes.com" <vincentcoste12 at gmail.com> wrote:
> Dear Trnsys users,
> 
>  
> 
> Before using TRNSys-3D, I thought the big advantage was the easy way to model shading masks by drawing masks directly on SketchUp (using shading groups function).
> 
> However, analyzing the results, I realized shading masks were not considered  by the model.
> 
> Is it normal ?
> 
> Did I miss an important step ?
> 
> Did one of you obtain results with shading masks drawn by SketchUp ?   
> 
>  
> 
> In addition, I don’t understand how shading masks are modeled (if they are modeled) : the simulation studio file created by the 3D-Building Project Wizard do not use types (like Type 67 or 68 or 34 …) so radiations from the weather file are not modified before the Type 56.
> 
>  
> 
> Thanks a lot for your answers !   
> 
>  
> 
> Best regards,
> 
>  
> 
>  
> 
> Vincent COSTE
> 
> 
> 
> 
>  