[TRNSYS-users] questions about Trnflow
    Angela Dröscher 
    angela.droescher at tugraz.at
       
    Tue Aug 17 04:28:01 PDT 2010
    
    
  
Hi,
I experienced exactly the same error when I tried to run the TRNFlow example that is distributed with TRNSYS 17. The problem was that the "simple" Type56 was used there instead of Type56-TRNFlow. Replacing this Type (-> \Loads and Structures\Multi-Zone Building with Air Flow (TRNFLow)) solved the problem in my case. Are you sure you employed the appropriate Type?
Best regards
Angela
-- 
Graz University of Technology
Institute of Thermal Engineering
Inffeldgasse 25/B, A-8010 Graz, Austria
Tel.: (+43) 316 873 7307
Fax: (+43) 316 873 7305
http://www.iwt.tugraz.at
Am 17.08.2010 12:51, schrieb 王洋:
> Dear all,
>
>   I have set up a very simple zone only including one airlink--Large Opening. But I run it, the list file shows Parameters for TRNFlow are missing. Please, check defined parameters! I only define one Opening with Daily Schedule, and I set up one Daily Schedule using Type 14, meanwhile, I define a Output NTYPEs 207 and link Type 65 with Type 56, I want to observe Output NTYPEs 207(total outdoor air flow into airnode). Only these, but the list file shows Parameters for TRNFlow are missing. Please, check defined parameters! I don't know what other Parameters are lack, if list file can tell what are missing, that's better. Do you think how to find missing Parameters ? Which Parameters are easy to be misses? Indeed I can not find them.
>
> Thanks!
> Br.
>
> wang
>
> ps.:the listing file shows:
>
>   TRNFLOW (2003-06-04) based on COMIS 3.1
>   Copyright (C) 2001   EMPA
>
>   -------------------------------------------------------
>   Note: as soon as TRNFLOW is switched on, all couplings
>   between zones which are not in the air flow network and
>   those included in the network are reset to zero!
>   -------------------------------------------------------
>   No SET-file; using defaults
>
>   *******************************
>   Reading Input File            *
>   *******************************
>
>
>   *******************************
>   Checking HVAC T-Junction data *
>   *******************************
>
>
>   *******************************
>   Looking for RF components     *
>   *******************************
>
>
>
> *** Notice at time        :         0.000000
>      Generated by Unit     :    56
>      Generated by Type     :    56
>      Message               : Star network calculation: every iteration step of TRNSYS
>
>
> *** Fatal Error at time   :         0.000000
>      Generated by Unit     :    56
>      Generated by Type     :    56
>      Message               : Parameters for TRNFlow are missing. Please, check defined parameters!
>
>
> *** An error has forced TRNSYS to abort
    
    
More information about the TRNSYS-users
mailing list