Dear Pablo,
 
the 3D detailed radiation mode of TRNSYS 17 are restricted to convexe
zones. 
Therefore no "internal walls" blocking views are allowed to be defined.
 
You may split your zone into convex several convex zones or increase the
capacity of the air node.
 
At the moment we are working on developing and incoorperating improved
algorithms which can 
handle concave zones. 
 
Marion 