Fred,
perhaps I need to see the project. If you are passing 22.2 dry bulb
and 14 wetbulb to Type33, it should just be spitting back the exact same
thing with a calculation of RH. I just tried that and I'm getting an RH
of 40% at 1atm pressure. When you say there is a 6.8C wetbulb, is that
on the other side of the energy wheel?
David
On 8/31/2010 09:19, Fred Betz wrote:
>
> I am passing 22.2 C dry bulb and 14.0 C wet bulb to the psychrometric
> routine (type 33f) and the output is 22.2 C dry bulb, 6. 8 C wet bulb
> and 0% RH, which is causing an error in the psychrometric routine for
> a total energy wheel.
>
> The output should be approximately 60% RH.
>
> The humidity ratio is also showing 0.0.
>
> Please advise,
>
> Fred
>
> *Fred Betz** *PhD., LEED AP
> Sustainable Systems Analyst
>
>
>
>
>
> *AEI* | AFFILIATED ENGINEERS, INC.
> 5802 Research Park Blvd. | Madison, WI 53719
>
> P: 608.236.1175 | F: 608.238.2614
> fbetz at aeieng.com <mailto:fbetz at aeieng.com> | *www.aeieng.com
> <http://www.aeieng.com/>*
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100831/1aa7743c/attachment-0001.htm>
More information about the TRNSYS-users
mailing list