[TRNSYS-users] questions about Trnflow
Mariëlle Nuchelmans
M.Nuchelmans at chri.nl
Fri Aug 20 02:26:07 PDT 2010
Hi,
It is just a warning. You define two different heights for an airnode: TO-height and FROM height. These two are in your case not equal, so trnflow treats it as a vertical shaft (to overcome the distance). If this is what you want, you can ignore the message. If this isn’t what you want (you’ve got an horizontal link) then you should check the to and from heights. See picture below (from trnflow manual)
[cid:image002.gif at 01CB405A.7BBC8DA0]
Kind regards,
Mariëlle
Van: 王洋 [mailto:wanghongyang1767 at gmail.com]
Verzonden: vrijdag 20 augustus 2010 11:07
Aan: trnsys-users at cae.wisc.edu
Onderwerp: [TRNSYS-users] questions about Trnflow
Hi All,
I run the TRNFlow, the listing file shows as followes: How to deal with them? Many thanks!
***** WARNING ***** UNIT 56 TYPE 56, TIME = 0.000E+00
COMIS MESSAGE ***** NOTE *****
&-NET-LINks: LinkID=L2 Type=WI_001 FROM(zone AN_001)=1. m TO(zone
EN_001)=0.m deltaH=-1.m. ZoneHeight+LinkHeight is different for sides FROM &
TO, like a vertical shaft. Is this OK ?
***** WARNING ***** UNIT 56 TYPE 56, TIME = 0.000E+00
COMIS MESSAGE ***** WARNING *****
From and To total height of this large opening link are not within 0.1m:
L2
----------------------------------------------------------------
***** WARNING ***** UNIT 56 TYPE 56, TIME = 0.000E+00
COMIS MESSAGE ***** WARNING *****
From and To total height of this large opening link are not within 0.1m:
L4
***** WARNING ***** UNIT 56 TYPE 56, TIME = 1.900E+01
COMIS MESSAGE ***** WARNING *****
Pollutant transport solver : Small timestep
needed (Tau < 10 sec), but is limited to 1 sec
----------------------------------------------------------------
If you know how to do with them,PLEASE tell me! I'm very urgent for them!
Thanks again!
BR.
Andy Wang
2010/8/19 <trnsys-users-request at cae.wisc.edu<mailto:trnsys-users-request at cae.wisc.edu>>
Send TRNSYS-users mailing list submissions to
trnsys-users at cae.wisc.edu<mailto:trnsys-users at cae.wisc.edu>
To subscribe or unsubscribe via the World Wide Web, visit
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
trnsys-users-request at cae.wisc.edu<mailto:trnsys-users-request at cae.wisc.edu>
You can reach the person managing the list at
trnsys-users-owner at cae.wisc.edu<mailto:trnsys-users-owner at cae.wisc.edu>
When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
Today's Topics:
1. TRNSYS Window Library (Daniel Bergey)
---------- 已转发邮件 ----------
From: Daniel Bergey <daniel at buildingscience.com<mailto:daniel at buildingscience.com>>
To: trnsys-users at cae.wisc.edu<mailto:trnsys-users at cae.wisc.edu>
Date: Thu, 19 Aug 2010 10:29:04 -0500
Subject: [TRNSYS-users] TRNSYS Window Library
I'm putting together a TRNSYS model for research on ventilation and
dehumidification. We have identified the windows we will use in terms of
SHGC and U-value, which of course isn't enough as inputs to Type56. The library bundled with TRNSYS does not have windows reflecting what we see in residential buildings.
I expect others have run into the same problem. Does anyone have window inputs that fit any of the following examples?
U-value (IP) SHGC
0.4 0.4, 0.35, 0.3
0.35 0.4, 0.35, 0.3
0.3 0.4, 0.35, 0.3, 0.25
0.25 0.35, 0.3, 0.25
Thank you,
Daniel
--
Daniel Bergey
Building Science Corporation
30 Forest Street
Somerville, MA 02143
978-589-5100 x 5277
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu<mailto:TRNSYS-users at cae.wisc.edu>
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100820/568f1c1b/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.gif
Type: image/gif
Size: 21325 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100820/568f1c1b/attachment-0001.gif>
More information about the TRNSYS-users
mailing list