[TRNSYS-users] Internal walls and Trnsys3d
Marion Hiller
hiller at transsolar.com
Wed Aug 4 02:28:06 PDT 2010
Dear Pablo,
the 3D detailed radiation mode of TRNSYS 17 are restricted to convexe
zones.
Therefore no "internal walls" blocking views are allowed to be defined.
You may split your zone into convex several convex zones or increase the
capacity of the air node.
At the moment we are working on developing and incoorperating improved
algorithms which can
handle concave zones.
Marion
_____
Von: Direccion [mailto:direccion at idienergia.es]
Gesendet: Dienstag, 3. August 2010 13:56
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Internal walls and Trnsys3d
Hello.
There’s no “internal wall” in “Constructions” when I try to draw a
building with Trnsys3d. I can’t add that walls inside Trnbuild 17,
because I need to use the 3D Model.
¿Somebody knows how can I model these types of walls and, at the same
time, model with Trnsys 3D?
Thanks to all.
PABLO EGUÍA
Director Técnico
IDi Energia.
C/Padre Ramón María Aller, nº 6, 1ºD
36201 – VIGO
Pontevedra
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100804/d5d0f724/attachment-0001.htm>
More information about the TRNSYS-users
mailing list