[TRNSYS-users] external file for type 53 (parallel chillers)
Martin Thur
Martin.Thur at BLS-Energieplan.de
Fri Apr 30 01:48:06 PDT 2010
Hello everyone,
I want to create an external file for type 53. According to the manual I have to calculate "the ratio of the temperature difference between the condenser water outlet and the evaporator water outlet relative to a specified design temperature difference". I calculated these ratios based on manufacturers data at the following chiller conditions:
- decreasing chilled water mass flow rate (representing part load)
- constant cooling water inlet temperature and therefore decreasing outlet temperature
- constant chilled water outlet temperature
My file then looks like this:
0.00 0.78 0
0.05 0.79 0.08
0.10 0.81 0.17
0.15 0.82 0.25
0.25 0.84 0.42
0.30 0.85 0.46
0.40 0.87 0.49
0.50 0.89 0.55
0.60 0.91 0.60
0.70 0.93 0.66
0.80 0.95 0.74
0.90 0.98 0.85
1.00 1.00 1
When I run the simulation I get an error at the time step the chiller is supposed to turn on:
"The chiller is operating outside of the range defined by the performance curve fit."
The question is now: Is the form of the file incorrect? (which I don't think) Or did I calculate the ratios wrongly?
Thank you in advance
Martin
Bei Fragen bitten wir um Ihren Rückruf.
Mit freundlichen Grüßen
BLS Energieplan GmbH
i. A. Martin Thur
Elsenstraße 106
D-12435 Berlin
Tel.: +49 30 53 32 81-0
Fax: +49 30 53 32 81-40
____________________________________________________
BLS Energieplan GmbH
Sitz der Gesellschaft: Berlin
Geschäftsführer: Christoph Lange, Wolfgang Sturm
Registergericht: Amtsgericht Berlin-Charlottenburg, HRB-Nr. 32021
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100430/c8ee084d/attachment-0005.htm>
More information about the TRNSYS-users
mailing list