[TRNSYS-users] Likely bugs in Type655 and Type666
a8304506 at graduate.hku.hk
a8304506 at graduate.hku.hk
Thu Apr 29 18:30:49 PDT 2010
Hello, all.
I previously developed a parametric model for a water-cooled chiller. I used it
to compare the results with those based on Type666. I then found that
calculated COP seemed to increase only mildly during the low-load period when
using Type666. I went through the source code and the related data files. I
found that the following statements appeared to be wrong:
COP_RATIO=Y(1)
CAP_RATIO=Y(2)
According to the data file, the first output should be the capacity ratio while
the second output is the COP ratio. The same case happened for Type655. Am I
wrong?
Best Regards
LEE, Chun Kwong
Division of Building Science and Technology
City University of Hong Kong