[TRNSYS-users] Type56 - TRNBuild error
David Bradley
bradley at tess-inc.com
Tue Apr 13 12:24:48 PDT 2010
Dear Mika,
Typically with thicker walls, you have to use a larger timebase; the
default is 1 hour and I notice that your building finds a solution with
a 1 hour timebase. The coefficients that are being generated for the
wall are basically weighted averages on the factors that affect energy
transfer through the wall (factors like temperature difference across
the wall). The weighted averages tell how important a particular factor
was one timebase before the current time, two timebases before the
current time, three timebases before the current time, etc. The thicker
your walls, the farther back into history you have to go in order to get
a full picture of how energy is transfered through the wall.
Coefficients are generated for the last 20 timebases; by using a 0.1h
timebase, you are only allowing TRNBuild to look back 2 hours. With a 1
hour timebase, you are allowing it to look back 20 hours. In your case,
the important response of the wall occurs somewhere between 2 and 20
hours ago.
Best regards,
David
Yoshinaga Mika wrote:
> Dear David and all,
>
> I'm modeling a RC-house with high insulation by TRNbuild.
> But putting the thick insulation layer into wall type makes TRNBuild Error
> window "Error creating the wall transfer function coefficients" pop up. The
> timebase is set as "0.1".
>
> I attached the bui file.
> * RCOUTWALL wall type has 150mm concrete layer and 100mm GW insulation layer
>
> * RCROOF wall type has 130mm concrete layer and 100mm GW insulation layer
> If you click "save" button, the error window pop up.
>
> How can I handle it?
> Thank you in advance!
>
> Kind regards,
>
> Mika Yoshinaga
> Meijo university, Japan
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
More information about the TRNSYS-users
mailing list