sure, if you have the global radiation in a horizontal surface (I guess
that's the one you have)...you can say
Ig=Id+Ib
where Id and Ib are diffuse and beam irradiances on a horizontal surface,
since you have the DNI and the elevation solar angle, and you know that Ib =
DNI*sin(elev)
you can say that
Id=Ig-DNI*sin(elev)
you can use a calculator to do so
regards
2010/4/30 Laia Cases - iMat <lcases at imat.cat>
> Hi Trnsys users,
>
> is there any way to obtain diffuse radioation from global radiaton data to
> be use to simulation studio?
>
> thanks in advance
> Laia
> --
> *Laia Cases*
> Unitat de Condicionament Tèrmic
> *iMat - Centre Tecnològic de la Construcció
> lcases at imat.cat
> www.imat.cat*
> Wellington 23 · E-08018 Barcelona
> T +34 93 553 97 95
> F +34 93 553 97 96
> Imprimiu aquest document només si és necessari
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
--
Jaime. González Rodríguez
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100430/06ce5069/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27188 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100430/06ce5069/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 30755 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100430/06ce5069/attachment-0003.jpeg>
More information about the TRNSYS-users
mailing list