[TRNSYS-users] A lot of convergence warnings
knut.erik.enerstvedt at niva.no
knut.erik.enerstvedt at niva.no
Thu Apr 29 06:55:04 PDT 2010
In addition to reducing time step length, I would try the following:
- Check if there is sufficient thermal mass in your system (add pipes in
fluid loops, for example).
- Use controllers (such as Type 2) instead of equations (LT, GT and
similar) when variables that can change from one iteration to the next are
involved.
- Place components in a "natural" calling order (controllers before
controlled equipment, for example): Control cards->Component order: Click
and drag the different components to order them.
- Use an online plotter to check if there are any unrealistic output
values (very high temperatures, for example).
Best regards,
Knut Erik Enerstvedt
>You could change the simulation time step (in steps of 1/(2^n) so 1 hour,
0,5 hour, 0,25 hour etc). You can find this by assembly -> component
>order.
>Good luck,
>Mariëlle Nuchelmans
>Hi,
>What can I do when there are lots of convergence problems??? The same
project has different warnigs because of that if the simulation >starts at
3896 than if it starts at 0.... Does the option "Optimaze component order"
work?? If I select that option other errors appear... :(
------------------------------------------------------------------------------------------------------------