[TRNSYS-users] Type204-PCM
David Bradley
bradley at tess-inc.com
Fri Sep 18 07:47:51 PDT 2009
Bezeid,
Because there is not a model for a PCM material built in to the Type56
building model, there needs to be some way for a Type that models the
PCM to interface with the rest of the building (for example so that the
inside surface of the PCM material can be part of the radiative and
convective energy balance of the thermal zone). The way that this
interaction is often achieved is to define a BOUNDARY wall in
TRNBuild/Type56. A BOUNDARY wall is a surface that interacts with the
zone on one side and has some known temperature on the other side. When
the BOUNDARY wall interfaces with an external Type (such as 204), the
temperature required by the BOUNDARY wall is the interface temperature
between the back of the BOUNDARY wall and the front of the PCM material.
Typically the way that the coupling is achieved is that Type56
calculates the inside surface temperature (TSI) and the amount of energy
being transfered through the BOUNDARY wall into the PCM (QCOMI and/or
QCOMO). These values are passed to Type204 as inputs; Type204 then
computes the reaction of the PCM to those inputs and calculates a new
interface temperature, which is passed back to Type56 as the BOUNDARY
wall's outside temperature. Iteration continues until energy balances.
Kind regards,
David
bezeid.deddy at orange-ftgroup.com wrote:
>
>
> Hello TRNSYS Users,
> I am Deddy bezeid and I make a thesis at the bretagne-sud university,
> I am a new user of TRNSYS and I encounter problems on the TYPE204 -
> PCM and I already found somebody who put the same questions with which
> I would like to have answers, here the questionnaires and thank you
> for your assistance
>
> I want to use TRNSYS Type 204 for the simulation of PCM layers on a
> building. Has anyone used this type before? It takes forever to run an
> one week simulation...However the main problem is i cannot understand
> the way the model simulates a PCM layer... My questions are about the
> SUNSPACE example supplied into the files package loaded : There are 2
> air zones in the TRNBUILD type 56 model of this example : SunZone and
> BackZone. SunZone is where "PCM wall" has been installed. So :
>
> - How to make the difference if we want "PCM layer" into all walls
> surfaces from SunZone, or only into some of them?
> - Why the resistance of the "PCM massless layer" created in TRNBUILD
> is only 0.1 m².K.h/kJ?
> - Why the "PCM wall" using the "PCM massless layer" into SunZone
> (boundary wall calling T_PCM input) presents a so small surface of 0.2
> m²?
>
> - Why QCOMI is taken from the same "PCM Wall" (14) and not from other
> walls?
> - Do we have to change values into the 4 text external files supplied
> (NodeTemp.txt, Tila.txt, Ceff1.txt, ALKU.txt) or do we only have to
> call their path?
>
> - Why the PCMeT (average surface temperature of "PCM wall")calculated
> by type 204 is sent to the boundary "PCM wall" input (T_PCM) into type
> 56 ?
>
> type 204 receives QCOMI from 0.2 m² surface (14), and T_AIR from
> SunZone volume,
> then it calculates and sends T_PCM to boundary input for 0.2 m²
> surface (14)
> => I don't see in which way this sequence allows modelization of PCM
> introduction into a wall?
> I searched all the mailing list but i just found the same
> questions..and no answers... Please help...Thanks in advance
> Deddy bezeid
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090918/5b5c8c10/attachment-0005.htm>
More information about the TRNSYS-users
mailing list