[TRNSYS-users] problem about the differential controller (Type2)

Kersken, Matthias Matthias.Kersken at ibp.fraunhofer.de
Tue Sep 15 23:35:43 PDT 2009


Hello Yin!

As far as I know this controller already switches when he would exceed his deadband on the previous output-setting.
This is to prevent the controlled variable from exceeding the upper-limit-value.
I suspect You have two options:
- Choose a bigger Daedband.
- Set in the "parameter"-card the "number of oscillation" to a non-odd value like 4 or 6 (not 5). This should make Your controller less willing to switch becaus if he's oscillating and is finding no solution he'll not change but stay on the same value.

Ich hope I could help You!

With regards,
	Matthias Kersken


---
 
Dipl.-Ing. Matthias Kersken
Wissenschaftlicher Mitarbeiter / Abteilung Energiesysteme
Fraunhofer-Institut für Bauphysik 
Institutsteil Holzkirchen
Fraunhoferstraße 10
83626 Valley
eMail: Matthias.Kersken at ibp.fraunhofer.de
Telefon 08024 / 643-204
Telefax 08024 / 643-366
www.ibp.fraunhofer.de
Dipl.-Ing. Matthias Kersken
Research Associate / Department Energy Systems 
Fraunhofer Institute for Building Physics 
Branch Holzkirchen
Fraunhoferstraße 10
D-83626 Valley
eMail: Matthias.Kersken at ibp.fraunhofer.de
Phone +49 8024 / 643-204
Fax +49 8024 / 643-366
www.ibp.fraunhofer.de
 
 
 
 
 
 
 
 
 
 
 
 
 
---

-----Ursprüngliche Nachricht-----
Von: Yin Hang [mailto:yhang at purdue.edu] 
Gesendet: Dienstag, 15. September 2009 17:08
An: 'Francois Badinier'; trnsys-users at cae.wisc.edu
Betreff: Re: [TRNSYS-users] problem about the differential controller (Type2)

Hello,
Thanks for your replying.
I have connected connect the output of the controller to its "input control function" (input 4).
But if you look at the example in TRNSYS - "DHSW", you will also find this fluctuation problem.(suddenly on and suddenly off, even still in the deadband).
Thanks.
Yin

-----Original Message-----
From: Francois Badinier
[mailto:francois.badinier at icax.co.uk]
Sent: Tuesday, September 15, 2009 5:11 AM
To: 'Yin Hang'; trnsys-users at cae.wisc.edu
Subject: RE: [TRNSYS-users] problem about the differential controller (Type2)

Yin,

Make sure you connect the output of the controller to its "input control function" (input 4). You link the controller with itself basically. This has to be done in order to get the hysteresis effect working (influence of the previous state).
With that done, it should work properly.

Regards,

François Badinier
Development Engineer
ICAX Ltd
1 Hatfield House
Baltic Street West
London EC1Y OST
francois.badinier at icax.co.uk
www.icax.co.uk




-----Original Message-----
From: Yin Hang [mailto:yhang at purdue.edu]
Sent: 14 September 2009 19:47
To: trnsys-users at cae.wisc.edu
Subject: [TRNSYS-users] problem about the differential controller (Type2)

Hello,
I have a problem when I use differential controller type2.
For example, I want to control my solar collector loop pump by using one of this controller.
My control logic is when the outlet temperature of my solar collector is higher than the inlet temperature of my solar collector 4C, the pump will be on; And when it is lower than the inlet temperature for 2C, the pump will be off.
However, I found the output control signal is fluctuated, such as it suddenly becomes off even the outlet temperature is 2C higher than the outlet temperature; and next timestep, it suddenly on.
Could you help me to fix this problem? I figure it is really bad since it is un-normal for my pump during true situation.
Thanks.



_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.409 / Virus Database: 270.13.99/2372 - Release
Date: 09/15/09
05:59:00








More information about the TRNSYS-users mailing list