[TRNSYS-users] changing convection coefficients in a simulation

David Bradley bradley at tess-inc.com
Tue Sep 8 09:07:43 PDT 2009


Leen,
  As with most other things in Type56, the internal convection 
coefficients can be set as a CONSTANT, and INPUT, or a SCHEDULE. If you 
have an algorithm for your coefficients, you can implement them either 
as an equation or as a Type and you can pass them to Type56 as an INPUT. 
If your algorithm has the same form as the existing Type56 algorithm (a 
powerlaw, I think), you can modify them by clicking on the "Properties" 
button in the main project window in TRNBuild.
Kind regards,
 David


leen peeters wrote:
> Dear all,
>  
> I would like to change the internal convection coefficients for 
> simulation with a multy zone building (type 56) to new zone-dependent 
> values. I suppose these values are set somewhere in the type 56 code, 
> but it is not clear to me where exactly to change them.
> Could anyone help me out with that?
>  
> Thanks in advance!
>  
> regards,
>  
> Leen
>  
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>   

-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090908/bae8cf3e/attachment-0005.htm>


More information about the TRNSYS-users mailing list