[TRNSYS-users] Modelling a greenhouse thermal screen by using aninternal window in Type 56
Matt Duffy
duffy at tess-inc.com
Thu Oct 29 04:29:06 PDT 2009
Dear Knut Erik,
Your approach sounds very good. Yes, you may set the thermal properites of the thermal screen in the Window TypeManager where you mentioned. For more information about the reflection coefficient, see page 59 of the TRNBuild manual, Volume6. I don't really see any other red flags in your approach, and I do think taking the absolute value of your air flow calculation would be sufficient to maintain the correct balance.
Best regards,
Matt Duffy
----- Original Message -----
From: "" >;knut.erik.enerstvedt at niva.no
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20091029/2e89e2cf/attachment-0005.htm>
More information about the TRNSYS-users
mailing list