The easiest way it to use the boolean functions - especially since ON
signals are 1's and OFF signals are zeroes.
For example, run the pump if it's after 8 am and before 8 pm. The current
time is 1:20 in the afternoon for example.
EQUATIONS 4
XTIME=MOD(TIME,24) ---> Gives back 13.5
OK_LOWERTIME=GT(XTIME,8) --> Gives back a value of 1
OK_UPPERTIME=LE(XTIME,20) --> Gives back a value of 1
ON_PUMP=OK_LOWERTIME*OK_UPPERTIME --> Only a 1 if both functions are 1
FYI You'll want to be somewhat careful with the ON/OFF functions being
equations - especially if they'll be used to control components. You can
get in a non-convergence situation fairly easily.
Jeff