[TRNSYS-users] About Convective Heat Transfer Coefficient of Wall
David Bradley
bradley at tess-inc.com
Fri Nov 20 11:19:44 PST 2009
Roberto,
In addition to the conduction through the wall, there is also
convection and radiation from the wall surface to the ambient. Changing
the convective heat transfer coefficient only directly changes the
convection part of the equation. Of course changing the convection will
change the surface temperature which will in turn change the radiation
part as well but that is an indirect effect. When you change the
convective heat transfer coefficient you will NOT notice a change in the
displayed wall u-value in the TRNBuild wall manager. This is because the
convective heat transfer coefficient is dynamic (changes throughout the
simulation) and the displayed value is static - so it assumes a combined
radiation/convection coefficient for both the inside and outside wall
surfaces. The only thing that you can change in TRNSYS 16 concerning the
radiative part is the wall's absorptance to solar radiation. You cannot
change its emissivity, which is set to 0.9 internally.
One algorithm for external convection is proposed in ASHRAE Standard 140:
(a0+a1*WindSpeed-a2*WindSpeed**2) [W/m2.K]
a0, a1, and a2 depend on the building material. For concrete, they are
a0=8.23, a1=4.00 and a2=0.057
Kind regards,
David
caria.roberto at tiscali.it wrote:
> dear users
> I have any doubts about Convective Heat Transfer Coefficient of
> Wall:
> 1) if I change it does thermal trasmittance change? On the "Wall Type
> Manager" below on value of wall trasmittance there are two standard
> values: those will be change with a new value of Convective Heat
> Transfer Coefficient of Wall?
> If I wanted to insert a custom value, does anyone know any formula to
> calculate the coefficient as a function of the difference temperature
> and wind speed? Have I also consider the radiative part?
> thanks in advance
> Roberto
>
>
>
> Trova il tuo Prestito OnlineConfronta le offerte di 15 Istituti. Consulenza gratuita. Importo fino a 60.000 €. Durate fino a 120 mesi
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
More information about the TRNSYS-users
mailing list