[TRNSYS-users] Re : Type56a: Adjacent zones with little of no wall

Yujun TAO aleck1314 at yahoo.fr
Thu Nov 19 04:38:57 PST 2009


Another way is use a wall without any resistance and the real surface. But I'm not 100% sure it's right.
Kind regards

Aleck




________________________________
De : Sabine Jansen - BK <S.C.Jansen at tudelft.nl>
À : PAUL COALES <coalespr at btinternet.com>; trnsys-users at cae.wisc.edu
Envoyé le : Jeu 19 Novembre 2009, 11 h 49 min 16 s
Objet : Re: [TRNSYS-users] Type56a: Adjacent zones with little of no wall


The only way I know is by adding a very small wall anyway, since zones cannot be adjacent without a connecting wall. This wall can be as small as 10 cm2, which hardly has any influence on the results. This way it is still possible to simulate coupling airflows between these zones (or couple them in TRNflow)
 
Kind regards,
 
Sabine

________________________________
 Van: PAUL COALES [mailto:coalespr at btinternet.com]
Verzonden: ma 16-11-2009 9:07
Aan: trnsys-users at cae.wisc.edu
Onderwerp: [TRNSYS-users] Type56a: Adjacent zones with little of no wall


I have a number of zones with little of no physical wall between them.  How do I represent this in TRNBuild?

Thanks
Paul


      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20091119/ca0cd80c/attachment-0005.htm>


More information about the TRNSYS-users mailing list