[TRNSYS-users] (no subject)
David Bradley
bradley at tess-inc.com
Thu Mar 19 09:20:21 PDT 2009
Giorgos,
I would stay with Type753 (heating coil) and Type508 (cooling coil) if
indeed that is how the building is being heated and cooled. I am not
sure how you are controlling the system but I would recommend putting
the zones into temperature level control and adding a thermostat that
turns on and off the flow to each coil depending on the temperature of
the zone (instead of calculating a zone load and then somehow imposing
that on the coils. You may also need to use some diverting valves
(Type11) to control whether the water from your heat pump is going to
the heating or the cooling coil.
Kind regards,
David
Giorgos Fragogiannis wrote:
>
> Dear all
>
> I am new user in trnsys and I try to simulate o ground source heat
> pump system connected to o 7 zone building (type 56), in order to
> study the interrelation between ground, HP (water to water), fan coil
> and building.
>
> My question is what type of fan coil I must used in order to meet the
> heating and cooling demand?
>
> Until now I tried to solve this problem by using type 753 and 508
> simultaneously, but it is difficult to controlled it!
>
>
>
> Is the right way to use of water to air heat pump (type 505), as fan
> coil or you have any other idea about this problem ?
>
>
>
> My Regards
>
> George Fragogiannis
>
> National Technical University of Athens
>
> School of Mining and Metallurgical Engineering
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090319/16358375/attachment-0005.htm>
More information about the TRNSYS-users
mailing list