[TRNSYS-users] CSHPSS - Is a seasonal storage really THAT usefull ??

REBILLARD, Clement (Stagiaire CRPE) Clement.REBILLARD at veolia.com
Tue Jun 23 02:44:01 PDT 2009


Dear users,

 

I am currently modelling and simulating CSHPSS with TRNSys and i built 2 models (see attached pics for hydraulic schemes) : 

1. A plant like the one in Friedrichshafen, with a water tank as seasonal storage (no DUCT storage).

2. The same but without the Seasonal storage (only Collectors - Buffer - Distribution Net).

 

For general info :

Seasonal storage : Type342

Buffer Tank : Type534

Demand : 1100 MWh/year

Collectors : 2200 m²

Seasonal : 4400 m3

Buffer : 100 m3

Mass Flow Rates in Collectors : 18 kg/hr/m²

Net Temperatures (depart/return) : 70/40 °C

I searched the Litterature and found that these values are quite OK for a CSHPSS. Should you think some of them are Over/Under-estimated, please let me know.

 

Solar fractions obtained for the 3rd year of use are the following :

1. 42.2 %

2. 32.7 %

I stop the simulations after the 3rd year because at that time, i observe a stationary behaviour. 

 

As visual results, I can clearly see that case 1. offers more Fs in winter months, so the seasonal behaviour is met when expected. However, considering the high price of a Seasonal Storage, and seeing such a poor gain in Fs for the whole year, I now wonder if a seasonal storage is that usefull ...

 

Have anyone ever asked himself the same question and experienced the same results ?

 

Many thanks,

 

Clement Rebillard,

For Veolia Environment

___________________________________________________________________________________
 
Protegeons ensemble l'environnement : avez-vous besoin d'imprimer ce courrier electronique ?
___________________________________________________________________________________
 
Les informations figurant sur cet e-mail ont un caractere strictement confidentiel et sont exclusivement adressees au destinataire mentionne ci-dessus.Tout usage, reproduction ou divulgation de cet e-mail est strictement interdit si vous n'en etes pas le destinataire. Dans ce cas, veuillez nous en avertir immediatement par la meme voie et detruire l'original. Merci.

This e-mail is intended only for use of the individual or entity to which it is addressed and may contain information that is privileged, confidential and exempt from disclosure under applicable law. 
Any use, distribution or copying of this e-mail communication is strictly prohibited if you are not the addressee. If so, please notify us immediately by e-mail, and destroy the original. Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090623/038ca44a/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Carlsheim-1.JPG
Type: image/jpeg
Size: 24509 bytes
Desc: Carlsheim-1.JPG
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090623/038ca44a/attachment-0006.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Carlsheim-2-Noseasonal.JPG
Type: image/jpeg
Size: 20214 bytes
Desc: Carlsheim-2-Noseasonal.JPG
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090623/038ca44a/attachment-0007.jpe>


More information about the TRNSYS-users mailing list