[TRNSYS-users] Mean radiant temperature of building zones

Cramer Silkworth silkworth at transsolar.com
Fri Jun 5 14:10:36 PDT 2009


Two ways I can think of:

1. The operative temp is calculated using MRT and dry bulb temp weighted 
50/50 by default, so you can just back-out the MRT from operative temp 
and dry bulb temps.

2. Output ntype 17 (TSI) of type 56 is the inside surface temp, you 
could output this for all your surfaces and calc the average that way, 
but this is more tedious.

-Cramer

J. Cramer Silkworth
Transsolar Inc.
Technical consulting for energy efficiency and user comfort in 
buildings.
Stuttgart - Munich - New York
134 Spring Street Suite 601
New York, NY 10012
212-219-2255
silkworth at transsolar.com
 

-----Original Message-----
From: a8304506 at graduate.hku.hk [mailto:a8304506 at graduate.hku.hk] 
Sent: Friday, June 05, 2009 3:30 AM
To: Trnsys discussion group
Subject: [TRNSYS-users] Mean radiant temperature of building zones

Hello, Trnsys users.

Does anyone know how to output the mean radiant temperature of the 
building zones in Type56?  Thank you!

Best Regards
LEE, Chun Kwong
Division of Building Science and Technology City University of Hong Kong










More information about the TRNSYS-users mailing list