[TRNSYS-users] type71 - parallel use

Jeff Thornton thornton at tess-inc.com
Mon Jun 29 12:39:32 PDT 2009


<I'm using type 71 for a solar hot water plan of 100m².
In the project, there are 50 collectors connected in parallel, each one
has an array of 2m² .
My question is weather I have to set the "collector area" to 100m² and
the "number in series" to 1 or I need to model each solar panel with a
proper 2 m²-component ?>

Set the total area to 100 m2 and the number in series to 1 as you proposed.

Jeff



Jeff Thornton
President - TESS, LLC

22 North Carroll Street - Suite 370
Madison WI 53703 USA

Phone: 608-274-2577
Fax: 608-278-1475
E-mail: thornton at tess-inc.com
Web: www.tess-inc.com




More information about the TRNSYS-users mailing list