You probably need to to write a component model for the chilled beams which will
output the chilled beam capacity based on the zone temperature, entering
chilled water temperature and chilled water flowrate. You have to define a new
gain type in Type56 and implement it in "Other Gains" which will read the
chilled beam capacity from the chilled beam model through the inputs of Type56.
The calculated new zone temperature can then be used as the input for the
chilled beam model for new iteration until convergence is reached.
Best Regards
LEE, Chun Kwong
Division of Building Science and Technology
City University of Hong Kong
Quoting giacomo satta <swin at hotmail.it>:
>
> Dear all, we are two students of Politecnico of Milan and we have a problem:
> we need to simulate chilled beams in trnsys but we are not able to make this:
> Does exist any application or any way to do this?
>
> Best regards
>