[TRNSYS-users] "No output's specified"...
David Bradley
bradley at tess-inc.com
Fri Jul 24 12:45:04 PDT 2009
Nocolas,
I was not able to run the project because I don't have the data file.
However, in your Type56, you need to reference the *.bui file, not the
*.bld file... instead of
Verandas_v2.bld
that field should say
Verandas_v2.bui
Kind regards,
David
Nicolas Heijmans wrote:
>
> Hello,
>
>
>
> When I run this very small model, I get a message from TRNBuild,
> saying that "No OUTPUT's specified. Please add at least one OUTPUT."
> This is very strange, because outputs are defined... and if I close
> TRNBuild, the simulation is carried out.
>
>
>
> Any idea about how to solve this issue ?
>
>
>
> Thanks,
>
>
>
> Kind regards,
>
>
>
> Nicolas Heijmans
>
> Belgian Building Research Institute (www.bbri.be <http://www.bbri.be/>)
> Av. P. Holoffe 21, B-1342 Limelette, Belgium
> tel. : + 32 2 655 77 87 fax : + 32 2 653 07 29
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090724/25c7fc09/attachment-0005.htm>
More information about the TRNSYS-users
mailing list